Introduzione
Vai al passo 1
A GFCI(Ground Fault Circuit Interrupter) or RCD(Residual Current Device) is a safety device designed to protect people from electrical shocks caused by ground faults. Ground faults occur when electrical current escapes from a circuit and flows through a person's body to the ground. RCDs work by detecting this leakage and quickly shutting off the electricity to the circuit.
Testing your RCD is an important step in ensuring its proper functioning and your safety. There are two commonly used methods for testing a RCD: Using the test button on the RCD or using a Duspol to apply a load between PE(ground) and L(phase conductor).
While using the test button on a RCD is a quick and easy way to test its functionality, it may not always be enough to ensure its proper operation. The test button on a RCD simply simulates a ground fault by creating an imbalance between the incoming and outgoing currents on the circuit. This test verifies that the RCD can detect a ground fault and trip the circuit, but it does not confirm that the RCD can handle a real ground fault.
By using a Duspol or any other device to apply a load between L and PE, you are simulating a real-world scenario where a ground fault occurs. This test verifies that the RCD can detect and trip the circuit when a person comes into contact with the current and provides a path to the ground. This test also helps to verify that the RCD is providing the required level of protection to prevent electrical shocks.
In this guide, we will walk you through both methods and explain the steps you need to follow to test your RCD. By the end of this guide, you will have a clear understanding of how to properly test your RCD and ensure its reliable performance, helping you stay safe from electrical hazards.
Warning
If your RCD covers your whole house, your whole house will lose power while you test it. Make sure that you don't have anything important, like a data transfer on your PC, running while you perform this test.
  1. How to test a GFCI/RCD, Locate your RCD: passo 1, immagine 1 di 2 How to test a GFCI/RCD, Locate your RCD: passo 1, immagine 2 di 2
    • Find your RCD.
    • If you have RCD outlets you'll have to look for outlets with two buttons on them.
    • If your RCD is installed in your breaker panel you'll have to look for a larger breaker with a test button on it.
  2. How to test a GFCI/RCD, Press the Test Button: passo 2, immagine 1 di 3 How to test a GFCI/RCD, Press the Test Button: passo 2, immagine 2 di 3 How to test a GFCI/RCD, Press the Test Button: passo 2, immagine 3 di 3
    • Press the test button.
    • The test button is usually coloured. If it is not, it is usually the only button or labelled "T" or "Test".
    • Contact an electrician to replace your RCD, if this did not cause your RCD to trigger!
    • To turn your power back on, you'll need to flip the lever back up, or press the reset button.
    • The reset button is usually the only other button on the device or is labelled "Reset".
  3. How to test a GFCI/RCD, Find your phase conductor: passo 3, immagine 1 di 1
    • Use a Duspol or a single-pole phase tester to find your phase conductor.
    • Tip: To increase visibility of the phase tester's indicator, touch PE or a grounded object with your hand. This should cause the tester's indicator to shine brighter or become more noticeable.
  4. How to test a GFCI/RCD, Apply a load between L and PE: passo 4, immagine 1 di 1
    • Use the load feature of the Duspol to apply a load between L and PE.
    • This will not trigger an RCD with a rated residual current higher than 30 mA, though you shouldn't have an RCD rated over 30 mA installed in your home, as that's the maximum permissible rated residual current for personal protection anyways.
    • If your Duspol does not have the load feature or if you do not have a Duspol, you can still test the GFCI by shorting the neutral to ground. However, to do this, it is important to ensure that a device is currently drawing power from the circuit being tested. This is typically the case in most household settings.
Conclusione
Have fun and be safe!
Sebastian